A alameen Member May 22, 2011 #1 i saw secondary side of dry type transformer is grounded.. y like tat?
stevebea Senior Member Location Southeastern PA May 22, 2011 #2 alameen said: i saw secondary side of dry type transformer is grounded.. y like tat? Click to expand... Delta primary wye secondary?
alameen said: i saw secondary side of dry type transformer is grounded.. y like tat? Click to expand... Delta primary wye secondary?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician May 22, 2011 #4 Hard to say with so little detail but probably to make it safe in case of a ground fault on the secondary side.
Hard to say with so little detail but probably to make it safe in case of a ground fault on the secondary side.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) May 22, 2011 #5 what the others said. See NEC 250.20 & 250.30