Sizing a breaker below MOCP rating
ElecEngbw
I have an HVAC unit with a MCA of 74A and MOCP of 90A. I have an existing 80A breaker I would like to use for this unit. How low below the MOCP can I size my breaker?
I need clarification - 125% of 74A is 92.5A, which normally you would go to a 100A breaker. But, 440.52 says not more than, so 90A would match the MOCP. But the quandary is, I am not supposed to load a breaker to more than 80%, which in this case I am.
Is the NEC assuming that it will not run continuously? If so, that's a heck of an assumption. :confused:
The 125% has already been factored in 74 * 125% = 92.5. Just look at the nameplate and choose an OCPD between the MCA and the MOCPD.
MCA = minimum circuit ampacity = recommended conductor size?
I would get the actual motor full load amp (FLA) and size CB based on article 430.
440.4(A) would require you to use the nameplate information.