I need clarification - 125% of 74A is 92.5A, which normally you would go to a 100A breaker. But, 440.52 says not more than, so 90A would match the MOCP. But the quandary is, I am not supposed to load a breaker to more than 80%, which in this case I am.
Is the NEC assuming that it will not run continuously? If so, that's a heck of an assumption.![]()
MCA = minimum circuit ampacity = recommended conductor size?
I would get the actual motor full load amp (FLA) and size CB based on article 430.