I like to confirm that installing (2) 2 conductor NM cable for a single ceiling fan with a light is a violation. If it is a single fan/light unit it has to have a 14-3 in order for it to be code compliant. Assuming that the unit has a wall controls.
I like to confirm that installing (2) 2 conductor NM cable for a single ceiling fan with a light is a violation.
That would assume that you are using both whites as grounded conductors and that they are connected together at both ends. There would be no need to connect them together at the load end ...one for the light and one for the fan, just like the hots. There would also be no reason to use both whites...just use the two blacks and one white.I think your right. 310.4 for your grounded conductor.
That would assume that you are using both whites as grounded conductors and that they are connected together at both ends. There would be no need to connect them together at the load end ...one for the light and one for the fan, just like the hots. There would also be no reason to use both whites...just use the two blacks and one white.
300.3(B) would permit that.
One sw, One 14/2 for the fan. One sw, One 14/2 for the light. No problem.
One sw, One 14/2 for the fan. One sw, One 14/2 for the light. No problem.
or unless i am not understanding 300.3(b)??
300.3 Conductors.
(B) Conductors of the Same Circuit.
(3) Nonferrous Wiring Methods. Conductors in wiring
methods with a nonmetallic or other nonmagnetic sheath,
where run in different raceways, auxiliary gutters, cable
trays, trenches, cables, or cords, shall comply with the provisions
of 300.20(B). Conductors in single-conductor Type
MI cable with a nonmagnetic sheath shall comply with the
provisions of 332.31. Conductors of single-conductor Type
MC cable with a nonmagnetic sheath shall comply with the
provisions of 330.31, 330.116, and 300.20(B).
You are not reading it far enough.
That said I agree with Chris about 310.4
Would this not parallel the neutrals from the sw to fan/light?
I think your right. 310.4 for your grounded conductor.
Are you saying that you must size the ground according to 250.122?
BTW said:Yes this is for a ceiling fan NOT an exhaust fan.
No , he mentioned 310.4 why would 250.122 have anything to do with it? 310.4 is for conductors in parallel. If the OP connects both white wires in the NM cable to the fan neutral then you violate 310.4. That is why Don suggested not connecting one white wire.
BTW, I was thinking bath fan/light. If this is a ceiling fan then I agree there is only one neutral at the fan.
Edward, what rule requires the second white insulated conductor from being connected at all, on either end?300.3(b)(3) refers to 300.20(b) and that article talks about individual conductors passing through a metal with magnetic properties...... I also don't see how 310.4 allows this installation.
All the fans I have hung over the years have a seperate neutral for the light kit. If not, think outside the box and install one. Personally, I would run 14/3 but some people count penny's instead of quality and time.