Take a look at the second part of 690.64(B)(2):
(2nd Part) In systems with panelboards connected in series, the rating of the first OCPD directly connected to the outputof the utility-interactive inverter(s) shall be used in the calculations for all busbars and conductors.
This reads to me that when an inverter is backfed to a panelboard (Either dedicated for the PV system or an existing house panelboard). And then backfed to a main service. That the 120% rule applies to the panelboard 1st and then to the main service.
Is that how you interpret this section?
(2nd Part) In systems with panelboards connected in series, the rating of the first OCPD directly connected to the outputof the utility-interactive inverter(s) shall be used in the calculations for all busbars and conductors.
This reads to me that when an inverter is backfed to a panelboard (Either dedicated for the PV system or an existing house panelboard). And then backfed to a main service. That the 120% rule applies to the panelboard 1st and then to the main service.
Is that how you interpret this section?