I am currently negotiating with an A&E company, that I feel is qualified and experienced in project of our size and type, to perform an Arc Flash Harzard Analysis. My specs originally included all panels in the 3 ph system to be analyzed and labeled. Costs were above expected, so to reduce I asked the vendor to cut out 208 v panels fed by xfmrs <125 kVA. That reduced cost, but now those panels will have no labels.
Also, the vendor suggested to cut the Protective Device Coordination study on the grounds that I have very few CB that would have adjustments and therefore have little control of the outcome, other than replacing equipment.
Any comments or suggestions before this deal gets sealed.
Also, the vendor suggested to cut the Protective Device Coordination study on the grounds that I have very few CB that would have adjustments and therefore have little control of the outcome, other than replacing equipment.
Any comments or suggestions before this deal gets sealed.