Service enterance conductors land right into the 100amp breaker. I left those wires attached to it, pulled the breaker off the panel, turned it on and checked the stabs. I was getting 240v through the breaker. So how could the breaker be bad? When I plugged it back into the panel, only half the panel is live. I checked 120v to ground on each leg of the buss, and only one side is working.
The same way you can check voltage at a receptacle and read 120V but when a load is on it, it goes to zero, because of bad connection or damaged conductor. I'm not saying you definitely have a bad breaker but it can happen. I've seen 2-pole breakers do that.
If you have 240v with breaker pulled off panel
but not when it's plugged in--is it possible that you only see 240v on your meter until you put a load on breaker? Maybe you thought of that and tried it installed in panel with all other breakers off.
That's what I was talking about.
			