So why can't we use an ocpd on the smaller gauge wires for their rated ampacity?
I know the nec say's not to, and I also know that the '11 lowered the ampacity of 12 and 14, but 12 is still rated 25a in the 75c chart.
The original question acknowledged that fact. The real question is to the technical reason for the code rule.Because 240.4(D) says we can't.
I asked the same question to Southwire back in 2007, this is the response I got...............
"The Circuit Breakers - 15, 20 and 30 amp- were tested as a system using #14, 12 and 10 awg wire. UL found that when testing a #14 on a 20 amp breaker, there were problems with the breaker not operating properly. The same with the #12 on a 30 amp breaker. The heat of the wire would cause the breaker to over heat which would cause the wire temperature to rise causing the breaker temperature to rise....... so, the NEC limited the conductor ampacity to help solve the problem.
It is what it is.............![]()
not for me240.4(D) is technical enough for me.![]()
not for me![]()
Well how about this one:
While in almost all cases the wire itself will handle 25 amps without a problem, but the terminations won't, the problem is the heating at terminals and transferring to the wire melting the insulation back, and also damaging the terminal, the wire will act as a heat sink and if it is not large enough will not dissipate enough heat away from the terminal, most circuit failures are at terminations, this would also explain the problems at breakers.
As always the terminations are a factor, but most breakers and some other items are rated at 75?C. If the 75?C wire and terminations cannot handle the 75? ampacity, then those ratings not real...just made up numbers not backed by physics and testing.Well how about this one:
Hurk,
Then there is the case of my brother in Alaska.
In the dead of winter,
he says that they can run 67 Amps through a #12,
and the conductor temp is only slightly warm to hold.
Sounds "safe" in terms of terminal temp ratings,
but obviously not up to code ! :happysad: