Why is isolated earthing conductor recommended for computer panels ?
Mostly it is a carryover from a time when power supplies internal to computers were believed to and may have caused RFI. Shielding of those power supplies were connected to equipment ground and RFI impressed upon the shield made the grounding conductors act as antennae. Running an isolated grounding conductor inside of metal raceway provided another "layer" of shielding.Why is isolated earthing conductor recommended for computer panels ?
N
It was my understanding the isolated ground was used to try to eliminate circulating AC currents on these type of data lines.
s.
I have not installed an Isolated ground for anything in over 15 years. The very large Hospital where I work has over 10,000 computers spread out at 4 main campus and over 20 remote sites. Would not even try to image how hard it would be to pull a ground wire from the 12th floor down to 3 floors below the first floor to the 12" water main.
They were big in the late 70's and early 80's. If the computer that a panel feeds is important [ya everybody tells us that their computer is critical ] it should be backed up by a large ups feeding the panel, a good surge protector then a ups for each computer. We have at least 40 isolating receptacles, both staight blade along with twist locks collecting dust in our electric shop storage room. tom grabowski
I asked my foreman what IG's were for and what they did, the way he explained it to me was IG's were used on sensitive equipment to prevent "noise" or harmonics from creeping back to the computers
In my honest opinion I don't think your foreman knew the answer and was just reaching for anything.
IGs do nothing about the harmonic currents that the electronic equipment produce.
And 'noise' well, that sounds pretty vague don't you think?
I actually installed IG's in a fine arts center a couple years ago, and I asked my foreman what IG's were for and what they did, the way he explained it to me was IG's were used on sensitive equipment to prevent "noise" or harmonics from creeping back to the computers (or whatever equipment the IG is for). So for this kind of equipment i always though of IG's as more or a 'drain' or a 'shield' then a proper ground.
Being a fine arts center there were a ridiculous amount of IG's so it seems to me like IG's aren't being phased out as Ron was hoping a few posts back.
I was going to screw a ground lug to the panel, but the plant mechanic bonded them to the neutral bar..................................................
Hopefully isolated grounding and oversized neutrals will be a thing of the past sooner than later when old boiler plate specs are updated for computer rooms.
they do this to make sure they have clean power you are running 60hz and creating a frequency change every second which in terms causes audio and visual equipment to become interrupted and that creates distrubances in video and audio recordings remember that most electronics run on DC and have rectifiers that do that change for them. And a larger grounding system in terms make those changes slightly faster with less interferance they also have so called noise filters just depends on the type of system.