Swamp_Sparky
- Austin, TX, USA
Why wouldn't it be acceptable?
Well, if it's not actually listed, a lot of AHJs would have a problem with that.
They can have all the problem they want, but unless they can cite a requirement for PV discos to be listed, they have to accept it.
My question is, would this component be acceptable or not in a US installation, or would it be up to the AHJ?
690.4(D) Equipment. Inverters, motor generators, photovoltaic
modules, photovoltaic panels, ac photovoltaic modules,
source-circuit combiners, and charge controllers intended
for use in photovoltaic power systems shall be identified
and listed for the application.
They can have all the problem they want, but unless they can cite a requirement for PV discos to be listed, they have to accept it. I find no such requirement.
That doesn't mean it doesn't exist. If you can cite otherwise, I would be glad to have been enlightened. That's mostly why I frequent this forum.