What is 'PV wire'?
If it is not also listed by a name found in Table 310.13 you cannot use it at all for NEC applications.
does the code dictate the use of one over the other in an outdoor setting?
I am concerned ... since my system is an ungrounded PV system.
Not exactly. That is one of 3 wiring methods permitted. It does not require the use of listed PV conductors, it permits them along with nonmetallic jacketed multiconductor cables and conductors in raceways.For ungrounded systems the code requires PV Wire. 690.35(D)(3)
Not exactly. That is one of 3 wiring methods permitted. It does not require the use of listed PV conductors, it permits them along with nonmetallic jacketed multiconductor cables and conductors in raceways.
Not exactly. That is one of 3 wiring methods permitted. It does not require the use of listed PV conductors, it permits them along with nonmetallic jacketed multiconductor cables and conductors in raceways.
Why is it that I typically see USE-2 chosen as a popular choice for PV cables as opposed to other conductors that may be sunlight resistant and rated for wet locations?
So if the module conductors are routed in an raceway does that mean they can technically be of THHN type?