minerman
Member
- Location
- Columbus, Ohio, United States
I have a 480V feed from a 700A switchgear to a VFD, disconnect and motor.
The motor is rated at 515 full load amps.
Someone else sized the equipment for this job and I'm trying to make sense of it and choose wiring.
The switchgear breaker is rated at 700A, which seems fine to me. The VFD's internal breaker is also rated at 700A, which also seems fine...
But, the VFD is being shipped with 2 parallel 350MCM conductors per phase on the load side (connected to the load terminals). I've been advised to use the same conductors from the VFD to the motor. This seems too low to me. That would be rated for 620A which is less than 1.25 x 515A, right?. Also, someone chose a 600A disconnect. That also seems too low for the same reason.
Am I missing something here?
The motor is rated at 515 full load amps.
Someone else sized the equipment for this job and I'm trying to make sense of it and choose wiring.
The switchgear breaker is rated at 700A, which seems fine to me. The VFD's internal breaker is also rated at 700A, which also seems fine...
But, the VFD is being shipped with 2 parallel 350MCM conductors per phase on the load side (connected to the load terminals). I've been advised to use the same conductors from the VFD to the motor. This seems too low to me. That would be rated for 620A which is less than 1.25 x 515A, right?. Also, someone chose a 600A disconnect. That also seems too low for the same reason.
Am I missing something here?