I've been trying to find the answer to this but no luck so far. I'm getting 2 different answers from 2 non inspectors. Can you run 200amp SE cable inside the service mast and what code applies to this? Thanks.
Chapter 9 Table 1, note 8. Why would you want to do this?
Pipe fill does not apply.
(2) Table 1 applies only to complete conduit or tubing systems
and is not intended to apply to sections of conduit
or tubing used to protect exposed wiring from physical
damage.
I've been trying to find the answer to this but no luck so far. I'm getting 2 different answers from 2 non inspectors. Can you run 200amp SE cable inside the service mast and what code applies to this? Thanks.
Same person said can't use #6 copper for gnd rods which I also thought was correct. Said had to be #4 copper for 200amp. What do you guys think of that one?
250.66(A)
Ahh, so his brain must have been thinking #4 alu wire and I thought #6 copper was right.
Ahh, so his brain must have been thinking #4 alu wire and I thought #6 copper was right.
Why not just run the SE like it was intended? just curious.... i know you asked a legit question.
How are you to terminate alum on a ground rod, especially if the rod is buried?
As far a using SE cable in mast, you could need a larger mast than if using individual conductors, will depend on cable dimensions. If mast is not used as a raceway there is no fill requirements.
If you are thinking about installing SER cable in an overhead riser I would suggest you reconsider.
We used to always use SER cable in service mast (and it always passed inspection) It seems that when you strip the sheathing off of SER to expose the individual wires for the utility to termintate to the wire loses it's "sunlight resistant" rating.
We got a lot of call backs on this exact type of install. Im not sure where your at, but in Florida it won't last 6 months and the insulation will be toast were it is subject to the elements!
If you are thinking about installing SER cable in an overhead riser I would suggest you reconsider.
We used to always use SER cable in service mast (and it always passed inspection) It seems that when you strip the sheathing off of SER to expose the individual wires for the utility to termintate to the wire loses it's "sunlight resistant" rating.
We got a lot of call backs on this exact type of install. Im not sure where your at, but in Florida it won't last 6 months and the insulation will be toast were it is subject to the elements!
This makes no sense to me? A SE or SER cable gets the sheath stripped back for POCO connection, whether in a pipe or not.
I was referring to was is stated in 250.66(A) on alu wire. Never used it.
Just curious, I always use XHHW conductors for meter risers. What type of indivual conductor
is in SE cable ?
You're not allowed to point out the obvious. Im guessing once you get into Florida, the SE/SER no longer can block out the sun.This makes no sense to me? A SE or SER cable gets the sheath stripped back for POCO connection, whether in a pipe or not.