You cannot use aluminum to a ground rod unless it is 18" above grade
Hmm, after reading 250.66 some more I'm somewhat confused now. 250.66(A) says #6 copper is fine for Gnd rods but the chart says for 4/0 alu which is the largest conductor in the SE cable would require #4 copper. Am I reading this correctly?
Pipe fill does not apply.
(2) Table 1 applies only to complete conduit or tubing systems
and is not intended to apply to sections of conduit
or tubing used to protect exposed wiring from physical
damage.
A mast complete between the meter and the weatherhead would be complete system so conduit fill limitations would apply. For a sleeve I agree with you.
You are reading it right. #6 to rods,plates and such, #4 to water, building steel, CEE.
I read 250.66(A) which yes says #6 for rods.
But then when you look at table 250.66 on the same page, it states for 4/0 alu wire(largest conductor in the 200amp SE cable), a #4 copper conductor is required.
I think I'm reading it correctly, am I?
Or does the table not apply when using rods? I only looked at the table because some here mentioned it.
Did you do a calculation to see if 2" is large enough for the SE cable to meet the maximum fill limitation?
What did the calc come to with a 2.5" mast?
Unless I messed up, my math says this cable would fit in a 2".
I used 4/0 AL SE from Southwire. OD of 1354 mils.
I got 1.44 square inches.
I've been trying to find the answer to this but no luck so far. I'm getting 2 different answers from 2 non inspectors. Can you run 200amp SE cable inside the service mast and what code applies to this? Thanks.
SE cable needs to follow the NM rules, cannot be installed in damp locations, a service mast is a damp location..NO
SE cable needs to follow the NM rules, cannot be installed in damp locations, a service mast is a damp location..NO
SE cable needs to follow the NM rules, cannot be installed in damp locations, a service mast is a damp location..NO