scottp628
- Pacific North West
looking for a manufacturer for a new fused distribution panel, single or three phase if one is still being made, Edison or plug style, not a circuit breaker panel for a small factory/research lab.
I see no practical reason for this request.
However, you might look at Cooper/Bussmann. They make a fusible lighting panel.
An owner or designer does not need to have a "practical reason" for his or her requirements.I see no practical reason for this request.
An owner or designer does not need to have a "practical reason" for his or her requirements.![]()
And then the EC can sell them a new systemSays who! It will be the Ec they go to when they are dissatisfied with what they have.
And then the EC can sell them a new system![]()
Fresh Market grocery stores use fusible panels in some of their stores, 20 amp branch circuits, it's been a while since I've seen one, but it kinda looks like a regular breaker, but has a switch that has a fuseholder built in. I can't remember if it was Square D, or some off brand, but it would work well in your situation. Uses high AIC cartridge type fuses. 277/480 volt service.
As the arc-fault protection issue came to the forefront of concern it has been argued that fuses are superior to circuit breakers in that aspect. The question of course is then: is it safer to reset a breaker or replace a fuse.
When it comes to fuses being replaced by non electricians the breaker is probably the better choice. Otherwise if the fuse will fit in the fuseholder and it has a bigger number on it than the one that it replaced, then that is the best choice (to the person changing it).
Luckily most faults, especially those on branch circuits, are L-G arcing rather than L-L bolted.... breakers are only rated/tested to interrupt a full rated SC only once, ....
breakers are only rated/tested to interrupt a full rated SC only once, so if you reclose it on a fault it is more likely to present a hazard than a fuse.
Are manufacturers of breakers not supplying the maintenance schedules for the breakers to follow? or Are the breakers not maintained properly by field people?
Yea the fist time they have a brown out or power failure and stuff blows fuses on start up he'll be singing the blues.
Does this company have a full time service tech.
Incredibly, some places in my country would specify that main disconnects use fuses and not circuit breakers