Client wants fuses no breakers, new service any ideas

Status
Not open for further replies.

RICK NAPIER

Senior Member
Location
New Jersey
If they want to use Edison-base fuses remember 240.51(B). If you show up and there is an oversized fuse in the panel it cannot be replaced. At that point the panel would need to be changed or S type fuses installed and they are a whole different set of problems.
 