Ampacity of Direct Burial Conductors
jason sleeth
Illinois
I have an installation in which the customer upgraded the size of his generator. I have installed a triplex "stephens" ALUM 2 awg, 7 strand, .403 inches. I have it buried under 36" in direct earth. The ampacity from the manufacturer states that it is good for 165 amp based on the NEC 2005. I need 145 amps. The length of the cable is 175'.
Can someone walk me through the NEC Calculation to determine the ampacity of the wire? I am unclear going through 310 on how to properly calculate the ampacity.
Thanks
There's a basic clash between "Stephens" and the NEC as "Stephens" is a UD cable and not a recognized NEC conductor, is not listed in Art 310, and normally is not acceptable on NEC covered installation.
Under NEC installs a #2 AL would normally be a 90 amp conductor.
For what it is worth, 145 amps, 175' 2AWG AL results in more than 7.2% voltage drop.
Unless this is the 'main feeder' to a dwelling unit 2 AWG AL is limited to 90 amps and you can't even roll it up to 100.
This is not a "walk through" situation. Calculation of ampacity for underground installations is a highly complex mathematical problem that involves dozens of variables. The bad news is that you need a computer program (those are not cheap) and a licensed professional engineer (we are not cheap either) to perform such a calculation. The really bad news is that the results are almost always lower than the values shown in table 310.16. So if you are hoping to get a little extra maneuvering room by using a calculated value, rather than a tabulated value, it is time to give up that hope. Sorry.
This is not a "walk through" situation. ,,,,,,,,,,,,,,,,,,,,,,,,,,,,,, and a licensed professional engineer (we are not cheap either) to perform such a calculation. ,,,,,,,,,,,,,,,,,,,,,,,,,,,,.
but , normally, worth every nickle.
The spec sheet states that it is UD but is rated for multiple insulations.
The spec sheet indicates the wire is ICEA s-105-692UL standard 854 for type USE-2 Federal Specification JC-30BNEC.
It also states that ampacity 90 degrees C, Conductor temperature 20 degree's celcius ambient, RHO50, 100% Load factor.
I am guessing the correct formula used for the engineer is 310.15 (C)
The RHO might be the value of thermal resistivity
I need to look through annex B then I will get back to you.
The amacity of conductors in free air greatly increases the amacity you are allowed on a conductor.
Direct Burial allows the heat to disapate in the ground plus the abient temp is about 57 degrees F
I do not think you are limited to the 90 amps in this scenario but that is why I am asking the more experienced electricians out there
You are right. There would be an issue with Voltage Drop. Thanks.