New member, please excuse if I tread on anyone?s toes.
I have a contractor saying, "they are not going to provide GFI outlets outdoors because the contract was bid on the 2005 NEC."
The outlets will be changed, the argument is, "who pays for the change." Contractor or Client?
The facility is industrial, a water reclamation facility,
My question, When did the NEC requirement for outdoor receptacles change to include all outlets outdoors?
NEC 2008 210.8 (B) Other Than Dwelling Units
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (5) shall have ground-fault circuit-interrupter protection for personnel:
(4) Outdoors
thanks, Bluetick1
I have a contractor saying, "they are not going to provide GFI outlets outdoors because the contract was bid on the 2005 NEC."
The outlets will be changed, the argument is, "who pays for the change." Contractor or Client?
The facility is industrial, a water reclamation facility,
My question, When did the NEC requirement for outdoor receptacles change to include all outlets outdoors?
NEC 2008 210.8 (B) Other Than Dwelling Units
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (5) shall have ground-fault circuit-interrupter protection for personnel:
(4) Outdoors
thanks, Bluetick1