And that will give us permission to leave the cable unsupported, yes.
Now, what allows us to leave it unsecured?
The same permission that allows it to be unsecured, (D)(1), not (D)(2)
And that will give us permission to leave the cable unsupported, yes.
Now, what allows us to leave it unsecured?
The same permission that allows it to be unsecured, (D)(1), not (D)(2)
I don't see how you can make a hole and then cover it up with a box and them claim inaccessibility.
Inspector- "You did not secure that piece of MC going into that box?" Was the place where it came through the top of the wall inaccessible?"
Electrician- "Yes sir. I screwed a 1900 box over the hole just to make sure."
Drill the hole above the stud cavity, place the box 1' or more away from the hole and strap the MC going into the box on the top.
Okay, if you are going to use 330(24)(D)(2) then I am going to have to give, but that limits the length of unsupported MC to six feet or less.
But neither the word secured nor unsecured appear in sub-section (D).
Sub-section (B) says, in part, "Cables containing four or fewer conductors sized no larger than 10 AWG shall be secured within 300 mm (12 in.) of every box, cabinet, fitting, or other cable termination."
What let's us skip that?
...
Edit: The main reason for securing & support in new work is to keep the cable away from the front of studs when the sheetrock is going up. In this case (old work) the sheetrock is already in place, no danger there.
Thank you Father.This is not a "sin" against the code, it is permitted. 330.24(D)
Thank you Father.![]()
How, pray tell, do you expect anyone to secure MC cable inside a finished wall....... through a 1" hole at the top? If this can be accomplished, I would really, truly love to see how.
Whether the hole has a box over it or not is not relevant. If the MC can magically be supported through the hole, then it can be done before the box is installed over the hole.
How, pray tell, do you expect anyone to secure MC cable inside a finished wall....... through a 1" hole at the top? If this can be accomplished, I would really, truly love to see how.
Whether the hole has a box over it or not is not relevant. If the MC can magically be supported through the hole, then it can be done before the box is installed over the hole.