hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
I was thinking about $800 for doing this (an hour out of town, but now i am more inclined to equate this with my charge for a panel change: $1600) i did a sub panel with a manual interlock (sweet cover came with it for real cheap) at $800 and i felt like i almost did it for free. it had a gen/recept under it too. This is a propane unit and needs to have conduit run to it outside the house. i think 1600 is about spot on. if that's not a contradiction.
I have found that many times transferring a whole house can be less labor then when doing the sub panel route, pulling the circuits out of the main panel and re-routing them into a sub panel can be a pain, so many times I find I can talk the home owners into a whole house system because the labor price can be that close that it will offset the cost of the larger generator and service rated ATS, especially when they have a outside disconnect that I can remove and install the ATS in place of it, but I don't do plumbing nor am I insured for it, so I always put it in the bid to be done by others, also when getting into 20kw generators and above watch out for the gas supply availability as some utility's will charge for up sizing the gas regulator and meter if more volume is needed, this is a big mistake that can cause warranty problems if the generator is underfed with fuel or the wrong size gas lines are run to it.