ptonsparky
Tom
- Occupation
- EC - retired
Industrial is expanding a building and local codes have changed enough that they are now required to provide at least a single line drawing of the electrical system to the city.  We put the service in years ago and the plant electrician has done the work since then.  They had installed a 601 amp feeder in preparation for this expansion and to feed some equipment along the way.  Three 2" emt conduits with 3/0 phase conductors and a #4 EG in each.  I mentioned that they should have had 1/0 EGs, if used.  Their question is "Remove the EGs completely, cut them off, or just leave it alone?"   (Most likely the building officials won't catch it anyway.)
	
		
			
		
		
	
				
			 
				
 
 
		 
 
		 
 
		 
 
		