You really need the compressor running load amps and the outdoor fan and indoor fan full load amps to calculate what goes in the panel. Using MCA for the panel load will give an inflated panel load if there is more than one A/C or if the A/C compressor is not the largest motor on the panel. There is no way to calculate running load from the MCA and MOCP values.
| [FONT=Times New Roman, serif]Voltage[/FONT] | [FONT=Times New Roman, serif]208V 			3Ph[/FONT] | [FONT=Times New Roman, serif]SupplyFan 			FLA[/FONT] | [FONT=Times New Roman, serif]16.7 			 (amp)[/FONT] |
| [FONT=Times New Roman, serif]Frequency[/FONT] | [FONT=Times New Roman, serif]60 			 (Hz)[/FONT] | [FONT=Times New Roman, serif]CondensingUnit 			FLA[/FONT] | [FONT=Times New Roman, serif]4.8 			 (amp)[/FONT] |
| [FONT=Times New Roman, serif]System 			MCA[/FONT] | [FONT=Times New Roman, serif]65.0 			 (amp)[/FONT] | [FONT=Times New Roman, serif]CondenserFan 			Power[/FONT] | [FONT=Times New Roman, serif]830 			 (W)[/FONT] |
| [FONT=Times New Roman, serif]System 			MOCP[/FONT] | [FONT=Times New Roman, serif]80 			 (amp)[/FONT] |  |  |
| [FONT=Times New Roman, serif]Compressors 			RLA[/FONT] | [FONT=Times New Roman, serif]38.0 			 (amp)[/FONT] |  |  |
| [FONT=Times New Roman, serif]Cooling 			FLA Total[/FONT] | [FONT=Times New Roman, serif]59.5 			 (amp)[/FONT] |  |  |
| [FONT=Times New Roman, serif]Unit 			Oper Range-Nom Voltage[/FONT] | [FONT=Times New Roman, serif]+/- 			10%[/FONT] |  |  |
Thanks for info this is what I found on unit can you explain what numbers I would actually use Thanks again
Your calc would be (59.5 amps x 208 volts x sqrt(3)) + 830 watts = 22,265.9 VA (round up to 22,266 VA).
Is this because this 59.5 is given for the full load amps of all fans, motors, etc.. running in the cooling unit?
I guess you want want to use this kW (or VA) vaule in a panel schedule because the MCA has an additional factor on it that is not necessary to include in the load calculation of the panel but rather is just for correct sizing of the circuit to the A/C unit?
Yes, the 59.5 amps is the sum of the 38.0 amp compressor, the 16.7 amp supply fan, and the 4.8 amp condenser fan.
So why add 830 watts for the condenser fan if the 4.8A for the fan is included in the 59.5A? Wouldn't 59.5x208x1.732 = 21.436kVA be more accurate?