ksmith846
 - Port St Lucie, Florida
A little help here please.......awarded a job recently and after we signed the contract the owner and GC asked us to offer any savings ideas we could.
One idea was to reduce the overkilled Grounding Electrode System as designed by the engineer. Their design was to install 30 feet of ground rod in a 30'x30'x30' triangular configuration with #4/0 bare copper to run between all 3 grounding electrodes to the footing steel and back to the service disconnect. Also to provide testing results to prove we met 5 ohms of resistance.
Considering the minumum code is to plant two ground rods with a maximum of #3/0 copper and tie to all available electrodes why are they requesting this installation. We have been taught via Mike's classes that Ground rods and GE systems are just to bleed off induced voltage from nearby lighting strikes....??
This is what the Engineering firm wrote to the GC and owner once they were asked to change the drawings to save the owner $$
"Our electrical design was intended to go above the minimal code requirements of 25 ohms, and was designed for the electrical system to be completely and effectively grounded with the grounding system not to exceed 5 ohms. We will not accept this VE change unless the owner provides a letter requesting the EOR's acceptance of this design change, and releases FAE from any potential issues resulting from electrical system not being effectively grounded."
Isn't my GE system completely and effectively grounded without having to reach 5 ohms with a huge triangular system?