If there was innerduct that was required to be run in the conduits and the spec read" All conduit/raceways by others" would you interpret that as the innerduct as well??..........but you were pulling the cables.

THanks.
 
If there was innerduct that was required to be run in the conduits and the spec read" All conduit/raceways by others" would you interpret that as the innerduct as well??..........but you were pulling the cables.

THanks.
Yes, I would interpret that as innerduct by others.
 
I would also consider the innerduct to be 'by others'.

I would consider that kind of raceway (770.12) to be included under the word "All".
 