Camers mounted outside on a pole. Is there a required depth/instalation for the camera wiring from the pole to the control? I noticed that on one of Mike's forums that it was stated that communicition wiring is not addressed in 300.5.
Coax article is 820, per 90.3 chapter 8 requirements are not subject to general requirements in chapters 1-7 unless there is a specific reference in chapter 8. There is no burial depth requirement for coax, damaging this is not going to cause an issue with fire.
Having said that, most would expect an electrical conduit to be 18 or 24" and thats what I would suggest.
If it is conduit I would think it would need to be below the frost line to keep it from damaging the cable?
While that would be code compliant it is not a true statement if you are working with rigid conduit or concrete encased non-metallic conduit. I have replaced conductors that were damaged by the "frozen wet conditions" a number of times. With the rigid or concrete encased raceways, when the water freezes, the expansion puts a large crushing force on the conductors and can damage the insulation and in the case of fiber, break the glass. In one case the freezing and thawing actual broke a 3 pair underground phone cable with a gopher sheild cable apart.... If it's rated for wet conditions, it's good enough for frozen wet conditions.