why when adjusting ampicity because of ambient temprature or sum of current carrying conductor we use 90 c column with thhn or thwn insulation although the conductor we have might have different insulation
For THHN/THWN you would use the 75? C ampacity in a wet location unless the conductor were also marked THWN-2.
That only applies if you are using the conductors in a wet location. THHN without the -2 is suitable for 90?C use in dry locations.Strictly speaking you only use the 90C column if the wire is THHN-2 or THWN-2, or something else with '-2' at the end, or something else that otherwise appears in the 90C column. ...
The THWN without the -2 is listed for 75?C in wet locations and 90?C in dry locations. See Table 310.13(A) in the 2008 code or 310.104(A) in the 2011.Can I ask why? Why does wet location change the de-rating column?
Also, I'm pretty sure THWN is rated for wet locations I was told that is what the "W" stood for. So if it is rated for wet locations why would you have to de-rate from a lower column?
Thanks Mike
If you don't know the answer to my question, it's all right.
Thanks Mike