Let me make sure I have got this right. In the event that no torque specs are listed on equipment Annex I column B is where I want to go?

For example I have 3/8" lugs, I would tighten these lugs to 375 inch pounds?

What does the N-m stand for? Is that a metric designator?
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician

Cloud

Member
Location
PH/VN
can some one help me to better understand the SLOT WIDTH and SLOT LENGTH mentioned on this table?
and is size #10 equals almost 5 mm?

regards!
 

Cloud

Member
Location
PH/VN
Please refer to my attached file, am I correct? Or the slot length is the diameter of the head and the one in the drawing is slot depth?We have done a mock up on a less than 10 screw and it seems the required torque stated on annex is not enough. I'm confused.
 