I have a 20 amp duples recepticle with the tab removed between the two hot screws  and feed with two twenty amp circuits. Is my device rated for two 20 amp circuits or is the whole device rated 20 amps. It feeds kitchen equipment toaster and waffle maker both at about 13 amps. 
One neutral going back to panel. Is my neutral then overloaded?
Thanks
	
		
			
		
		
	
				
			One neutral going back to panel. Is my neutral then overloaded?
Thanks
 
				
 
 
		 
 
		 
 
		 
 
		 
 
		