- Wisconsin
- PE (Retired) - Power Systems
Youngster, trying to show off?I would guess if I told you I once built a radio with a "cat's whisker" you would know what I meant huh?![]()
How big of an antenna did you use?
There seems to be a lot of 5th harmonic.
How are the capacitors connected?While I was there I talked to a few employees, I asked about failed ballasts and it turns out that is not really an issue. But they did have a pile of capacitors that they had replaced on HVAC unit motors.
Let me just ask a what if.
Lets say these HVAC units where rated for 240 supply but someone relabeled them 277 and they where supplied at 277.
Could I expect capacitor failures or would you expect another mode of failure?
OK. Did a bit of digging and I believe that Gar is correct for single phase motors.I am sorry I can't answer that.
120122-1632 EST
So I don't really know what that 156 V transient means. But it only occurred on the one phase and once within your test time frame.
A maximum peak pulse voltage would be a useful measurement.
