I just read an article on EC&M and they mentioned value engineering areas and they mentioned VE areas for switchgear and panels and they listed the following as potential savings:
1. AIC ratings
2. Feed thru lugs
3. Bolt on as compared to Snap in.
What determines when feed thru lugs can be incorporated into the design? Is there code that also comes into play?
How would you purpose an AIC change to something other than what the schedules show. If the engineer came up with those ratings isn't that final based on some sort of calculations.
If bolt on are cheaper why ever use snap in? Are most commercial panels nowadays bolt on anyway? Thanks
1. AIC ratings
2. Feed thru lugs
3. Bolt on as compared to Snap in.
What determines when feed thru lugs can be incorporated into the design? Is there code that also comes into play?
How would you purpose an AIC change to something other than what the schedules show. If the engineer came up with those ratings isn't that final based on some sort of calculations.
If bolt on are cheaper why ever use snap in? Are most commercial panels nowadays bolt on anyway? Thanks