What is the rating and configuration of the equipment being fed? I'd have thought that would pretty useful for determining transformer rating.I have a 100 amp service that is supplied with 120/208 volt single phase. I need to have 240 volt for the equipment being fed. What type and size transformer do I need to get my 240 volts?
I'm curious about that.The OP does specifically state the service is supplied with 120/208V single phase, and as such the voltage is stated properly.
It's two hots and a neutral fed from a wye secondary instead of three.
The 208V and the 120V sources would not be in phase though if they are derived from a 3-phase 208/120 system.Where I've seen it is, for example, a guard shack on an industrial site. You run a single phase feeder from the plant to the shack. You use the 208 for the heating and the 120 for the lights and the electronics.
Joe, I hope you mind that I've cut down you image to the basics.Just so we are all on the same page here. This is what his transformer connections would look like
Joe, I hope you mind that I've cut down you image to the basics.
![]()
So what do we have?
V bc, Vbn, Vcn
All at different phase angles.
Difficult for me to construe that as single phase.
I see what you are saying. In effect it is sort of an open delta