No splicing for grounding conductors

Status
Not open for further replies.

liverpool

Member
I am working on a project where the client's design criteria has a strict requirement of NO splicing what so ever for ALL grounding conductors. I am pretty sure that it's not a code requirement. Why would anyone require that? Any thoughts?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
How in the world are you going to install an equipment grounding conductor with a branch circuit without splices?:?

Chris
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
It must be fun to make up specs willy nilly with no idea as to how it'll get done as well as how much more it'll cost them.
 

btharmy

Senior Member
Location
Indiana
That would require a dedicated equipment grounding conductor to EVERY device (switch and receptacle) and piece of utilization equipment (light fixtures, hvac, etc) on the job. So a 277v. circuit with 30 fixtures and 12 switches would require 42 grounding conductors. Thats 42 grounds, 1 hot & 1 neutral just for one circuit. Impossible in my opinion. He MUST be speaking of the G.E.C. and not the equipment ground. A simple typing mistake or mis-understanding of proper terminology. If not, he's an idiot.
 
Status
Not open for further replies.
Top