Alwayslearningelec
- NJ
- Estimator
Just read this on EC&M website.
Grounding a parking lot light
I keep hearing that you shouldn’t use a ground rod at a standard metal parking lot light and that you should use an equipment-grounding conductor run with the circuits. The specifications for the project I’m working on now require both grounding methods. Is there a problem with this, and will I have to install two rods if I don’t have 25 ohms to ground?
The NEC requires the equipment-grounding conductor to be run with the circuit conductors, but it does not prohibit the use of auxiliary grounding electrodes, such as the ground rods. Section 250.54 repeats the requirement shown in 250.4(A)(5), where it states that the earth shall not be used as the sole equipment-grounding conductor. These auxiliary grounding electrodes do not have to be bonded to the grounding-electrode system as shown in 250.50 and do not have to meet the resistance requirements of 250.56. There are many pros and cons concerning the value of the auxiliary grounding-electrode ground rods for metal poles. They are of no value in providing a low-impedance ground-fault path to de-energize the circuit, but they may be of some value in providing a path for lightning strikes. Apparently, the specifiers think so.
So reading this article and the NEC a separate ground always have to be run with conduits for light poles. I am reading definitions in section 100 of the NEC. If a circuit has 1 phase wire, 1 neutral and a ground that may not necessarily be the EGC? That could just be considered the ground. What differentiates a regular ground from a EGC?