gar
- Ann Arbor, Michigan
- EE
120201-1026 EST
A correction to some statements I have probably made without my going back and rereading them.
I believe I may have related RMS current to power without considering the square factor.
When we modulate the sine wave with the on-off square wave, then if it is a 50% duty cycle the power drops in half and the reading of the average reading meter drops in half. But the RMS reading meter only drops to 0.707 times the continuous reading.
If continuous reads 1 A, then the average reading meter reads 0.5 A, and RMS reads 0.707 . If the duty cycle is 1/3, then the average reads 1/3, and RMS reads about 0.58 .
The check for DC current is an important test to determine whether the circuit is working correctly or not. But not a sufficient test.
ArchieMedes is the RMS meter not reading 1/2 the problem you are encountering with the clamp-on probe?