120127-2351 EST
ArchieMedes:
You have stated that your load is a resistance. Thus, the voltage across the load is equivalent to measuring the current. Just a scaling factor. I = V/R. The SCR controlling the current with a resistive load has nothing to do with whether you determine the current my measuring the voltage across the load or you directly measure the current. Measuring the voltage across a resistance as a shunt in series with the load or across the load is probably better than using a current transformer.
What a frequency measurement might tell you is the relation of no current to current, but it might not work well based on how the frequency meter worked. If positive crossings in a given time period are counted then it could work well.
The advantage of using a voltmeter to measure current is that greater overload capability exists. Also for a current probe that is rugged you could use a Hall device probe and it can work from DC to high frequencies with less phase shift problems.
I do not see any particular need to prefer average reading or RMS in your application.
What is the maximum on duration, how many full cycles if more than one, and maximum off duration in full cycles?
From any information you have provided so far you never half cycle, there is no phase shift control of the turn on time within a cycle (turn on is only at a positive zero crossing). Automatically SCRs or Triacs turn off at a zero crossing, and your implication is that this always occurs on a positive zero crossing.
.
We never half cycle, the triggering device makes sure that the SCR is always triggered on the zero crossing and as a minimum should complete one cycle. The maximum or 100% is the mains frequency 50 or 60Hz, it means SCR is always turned ON.
We measure the current in order to VERIFY or TEST the SCR and its triggering device is working properly. The full load current (mains voltage / resistance) is the maximum or 100%. If the SCR is triggered to 50% or one cycle on and one cycle off, the current reading should be half the full load current. That is the method or procedure to test so when we calculate the, let''s say, 50%, we are measuring different reading (mostly higher) than the calculated half of the full load current. Either the SCR or the triggering device is faulty but I am sure it is the measuring equipment as the readings are different with every current ammeter we used.