DavidA
Member
- Location
- Fresno, CA
I have just found out that I need to get educated about classified locations and associated wiring methods in a hurry. Does anyone have any suggestions for education materials?
It's industrial work in a food processing Mill. The classification is II, div 1 and 2. Up to this point in my career, I've never had to work in an area requiring classification so I'm completely unfamiliar with the wiring methods associated with these locations.
How about LFMC?Well, I just spotted the reference to flexible connections and zeroed in on that (2008) 502.10(B)(2). As I'm sure I mentioned somewhere in here I am completely ignorant of wiring methods in classified locations and am just making a shot in the dark as I read through the code. I didn't see LTMF as one of the approved wiring methods but saw MI under flexible connections. I am completely open to suggestion on this one as to methods of getting from RMC to a motor. I see that type TC is listed as an approved wiring method but I don't know if I can use that (with the appropriate connectors of course) in place of MI.
Okay, I'm begging now. What would be some other approved methods for connecting motors in a Class 2 Div. II area?
OP. One of the pitfalls of the NEC is that it does not generally tell you how to do something. It just give you parameters of a safe and hopefully functional installation and allows you to decide what materials methods and means are best suited for your exacgt situation.
Class II? Dust? Piece of cake.
The main concern is that nothing get hot enough to ignite the dust that's piles atop it. Most TEFC motors are rated for such use.
You'll probably encounter more problems with this being a 'food' site. USDA has all manner of concerns. In practical terms, it means everything is mounted somewhat off the wall (for cleaning and to prevent goop from accumulating), and that it be able to withstand the rather harsh chemicals used for cleaning and sanitizing. Again, in practical terms, that means using Noalox on your threads- and NO aluminum.
Some may call that a pitfall, others see that as a way of having more options. What if NEC told you exactly how to do things - you think you would have many options of how to do things?