Does the code say anything about using extension cords, hard wired into a panel, for permanent use? I've always been told this wasn't code legal, but I cant find any reference of it in the code book.
Do you really mean flexible cords?Does the code say anything about using extension cords, hard wired into a panel, for permanent use? I've always been told this wasn't code legal, but I cant find any reference of it in the code book.
For example, I created an outlet at my exterior, surface mounted panel by simply extending a short length of cord out the bottom of the panel with a cord cap on it. Even today, such an install might be allowed
I would fail it based on 400.8(1).
So is 400.7 mandatory to be used in the manner specified in the NEC. In specify #?s 1-10 where (B) also plays a roll? In other words, you can?t do what renosteinke done. Which was terminate a cord directly to a breaker of a panel ?I would fail it based on 400.8(1).
I started using these instead of extension cords.![]()
I agree with that.
Maybe he considers it a pendant.:happyyes:
The mentioned carnivals are temporary installations and subject to 590. (If someone was to inspect them to NEC compliance anyway)
Similar amusements at a permant park are not connected with flexible cords. They may have some cords where Art 400 allows them.
I would fail it based on 400.8(1).