Unfused Sevice Entrance

Status
Not open for further replies.

cdslotz

Senior Member
Up until the 80's, in Dallas you could run as far into the structure unfused, as long as it was in GRC.
There are tons of older buildings where the overhead POCO drop his 5-6 weatherheads and takes off 50=200' into the buildling.

No kidding
 

readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
I've worked on houses where poco hits weatherhead, entrance cable enters attic, leaves attic opposite end of house, drops to meter, entrance cable enters house and strapped 1/2 way thru crawlspace, finally gets to main in panel. Athens, Georgia '60s era is one that comes to mind.
 

RICK NAPIER

Senior Member
Location
New Jersey
Here we generally allow only a few feet. Just enough to enter the building and head right for the panel. We don't allow any additional length for RMC. I had one site that a short in the panel led to a melt down of the service feeders. It melted 3" off a 4" RMC that didn't even have any conductors in it.
 