I think the intent of the code is to afford protection against arcing faults and blasts and so the OP is not prohibited to provide a GFPE?I think the NEC only requires GFPE on equipment 1000 amps or greater.
The requirements are in 230.95.
230.95 Ground-Fault Protection of Equipment. Groundfault
protection of equipment shall be provided for solidly
grounded wye electric services of more than 150 volts to
ground but not exceeding 600 volts phase-to-phase for each
service disconnect rated 1000 amperes or more.
That is true. Not prohibited but not required either. The OP is also in the philippines so who knows what they require.I think the intent of the code is to afford protection against arcing faults and blasts and so the OP is not prohibited to provide a GFPE?
The OP may then highlight his requirements.The OP is also in the philippines so who knows what they require.
As taught, the setting for the GFI is 20% the max amp of the panel. We have 250A 380V panel.
Its called 'pick and click'. It basically ignores the fact that the GF relay is part of a system of protective devices....do any of our engineer's have some feedback about this 20% setting...
Ignoring the code not requiring the GFPE in 230.95 - what about the OPs querry about the 20% setting? I am not familiar with this...do any of our engineer's have some feedback about this 20% setting? Thank you in advance
You have a 250 amp Main Circuit breaker at 480 VAC, with Ground Fault Protection?
Ideally the design engineer should provide the setting of the GFP relay as part of the coordination study, unfortunatly in my expierence 99% of them skip that little bit of work.
Is there GFPE upstream of the 250 Amp CB?
Is the GFPE part of the circuit breaker?
What are the available setings, current and time delay?
What is the maximum size CB in the panel to be protected, excluding the main CB?
If you did 20% or 50 amps, everytime you had a ground fault on a branch circuit the main would trip.
The panel is being use by production, we cannot afford any tripping.
Thanks!
Then hire an engineer to perform a coordination study. If it is so important perhaps trusting a bunch of yahoos in the web is not the best idea.
Then hire an engineer to perform a coordination study. If it is so important perhaps trusting a bunch of yahoos in the web is not the best idea.
Yeah But we can trust you right?....:thumbsup:
Without all of the system info needed to do a coordination study anything anyone, including me, says is just a WAG.