Portable extension ladders...where is this info found?
97catintenn
Columbia, TN
My question was:
Using a portable extension ladder, how far above the elevated surface must your ladder extend?
Answers
2.5 ft
4 ft
I can't find the info. What book is it in?
It is an OSHA requirement and I thought it was 3', so the answer may be 2-1/2'
3' may have been one of the answers. thanks.
The answer must have been in the 'Code of Federal Regulations' which I do not have.
I do not really understand the question, are you referring to the overlap? From osha:
1910.26(a)(2)(iii)
Based on the nominal length of the ladder, each section of a multisection ladder shall overlap the adjacent section by at least the number of feet stated in the following:
______________________________________________________
Normal length of ladder (feet) | Overlap (feet)
____________________________________|________________
Up to and including 36 .............| 3
Over 36, up to and including 48 ....| 4
Over 48, up to 60 ..................| 5
You can access the cfrs for free here:
http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_id=9718&p_table=standards
OSHA 1926.1053(b)(1)
When portable ladders are used for access to an upper landing surface, the ladder side rails shall extend at least 3 feet (.9 m) above the upper landing surface to which the ladder is used to gain access; or, when such an extension is not possible because of the ladder's length, then the ladder shall be secured at its top to a rigid support that will not deflect, and a grasping device, such as a grabrail, shall be provided to assist employees in mounting and dismounting the ladder. In no case shall the extension be such that ladder deflection under a load would, by itself, cause the ladder to slip off its support.
damn i am dense this morning, i completely misread the question.:slaphead:
upper landing surface to which the ladder is used to gain access=elevated surface.:dunce: