Ever wonder why POCO's can do things like this :
		
		
	
	
		
	
		
	
And we have to size wire for services in accordance with the size of the main breaker installed and then de-rate and down-size wiring in accordance with 310.16 when we install sub-panels ?
And yes, they're feeding 6 services of various amperages (all 120/208 3 phase but probably not larger than 100 amps each) off the same feeder and transformers:
		
	
I don't know what size the feeder quad-plex is but it seems small by the standards we have to comply with. It's been working a long, long time so I guess it's sized correctly by POCO standards
	
		
			
		
		
	
				
			
	