What is the minimum size THW,or THHN conductor that can be used to wire an 80 kvr,3/0 460 volt Cap.
Help me on this one . Mike doesn't have anything in the work book.
infinity
New Jersey
Journeyman Electrician
Try this formula to find the current then use the reference 460.8 to find the minimum conductor ampacity.
I=kva/(E * 1.73)
Hv&Lv
Engineer/Technician
that is what I got.
Start by converting 80kVA to amps
I do either POCO calcs. or residential only.
The POCO calcs are a little different that NEC calcs. With that said, I want to see if I can get this right. Jumper, 135.7? Which comes out to 1/0. (75?) Yes or try again...
Flight987
I Did some Cal.
I Did some Cal.
I took 80000/(460x1.732 =796.72) So 80000/796.72=100.41 Amps. So 460.8 said thing's I don't understand.
I don't get this at all. Your turn.
jumper
Use 480V not 460.
460.8 says that the capacitor supply wires must be 135% of capacitor load rating, so multiply your number by 1.35 and then pick a conductor from 310.16.
Little Bill
Tennessee NEC:2017
Semi-Retired Electrician
Use 480V not 460.
OP said 460V. IMO, you can use that kind of like you are allowed in TBL 430.250. But it comes out the same either way.:thumbsup:
Little Bill
Tennessee NEC:2017
Maybe, I was taught to always use the listed nominal voltages for calcs. IDK.
It's not written/stated under the capacitor section but it seems similar since caps are often used in a motor circuit. The motor FLC tables state that you can/are permitted to use system voltage ranges of 110-120, 220-240, 440-480V, etc.
If the OP used either 460v or 480V it still works out. If he can grab hold of the basic formula that is.