NFPA 54: Section 7.13.2
The 2009 edition of NFPA 54 was approved by ANSI on September 5, 2008.  The 2009 editions of the ICC International Fuel Gas Code and the IAPMO Uniform Plumbing Code also have exactly the same language and requirements.  The latest editions of these codes require the
following:
7.13.1 Pipe and Tubing Other Than CSST. Each aboveground portion of a gas piping system other than CSST that is likely to become energized shall be electrically continuous and bonded to an effective ground-fault current path.  Gas piping other than CSST shall be considered to be bonded when it is connected to appliances that are connected to the appliance grounding conductor of the circuit supplying that appliance.
7.13.2 CSST. CSST gas piping systems shall be bonded to the electrical service grounding electrode system at the point where the gas service enters the building.  The bonding jumper shall not be smaller than 6 AWG copper wire or equivalent.This requirement should be enforced on all CSST brands and installations regardless of the fuel gas code in effect within the state, or the particular edition of the state code, and in addition to other gas piping requirements that are stipulated within the state fuel gas code.  This is a selfimposed requirement stated through the CSA standard and listing, and the installation instructions of each manufacturer.  In other words, compliance with the 2009 NFPA 54 should be in effect for all CSST brands for all installations in all states starting September 5, 2008.
There were no exemptions included or implied by these bonding requirements.