The issue is current punching holes in the wall of the tube. If there is not enough current no hole is made. How does giving it a better path to ground limit the current? In my opinion a better path to ground makes the problem worse, not better.
Don, it is not the current that is punching hole but where there is an arc to either another metallic pathway or even between the ribs, As we know (or should know) lightning is a high frequency event, and many bonds over 10 or 15' serve no useful purpose as these can be very high impedance to lightning, so much so that it has been found that even the distance from one rib to the next can have a difference of potential that the lightning doesn't even have to jump to another path as it can cause the holes just by arcing between the corrugated ribs.
In the last day I have been doing some searches and I have found a couple sites that say NFPA is trying to block the usage of CSST but as it was said it will take many years as much testing has to be done, the problem is the fire reports, most are not done by someone failure with the CSST problem and vital info is being left out.
but as I stated above, I believe that in time the truth will show that this stuff needs to be removed from the market.
I agree with you that just one bond at the entrance of the gas system or to the connector of the CSST will not prevent damage from lightning, it might prevent a few, but we can't go on just a few, it is ether safe or not, one life is one life to many if lost to this tubing.
The link in stickboys post, if you look at the bonding diagram on page 10 that was part of the settlement and see how much bonding they have done, this is much of what I have posted many times on here, providing an alternate pathway from the chimney and other appliances that would allow much of the current and voltage from a lightning strike to flow around the CSST is one of many ways that it would take to half way make this stuff safe, oh and those bonding conductors are much larger and braided flat copper, not just #6.
So in my opinion the cost of properly bonding as has been done in the aforementioned diagram would most likely make CSST not so cheap anymore