Alwayslearningelec
- NJ
- Estimator
What are the pros cons are running single conductor large size cable or a triplexed cable? DOes it make a difference if it were 15kv? Thanks.
The pro is having only one reel. Obviously much easier to feed from one reel than 4 separate ones.
The con? It can get a PRETTY big wheel when you have 3-4 conductors. And PRETTY HEAVY if you're pulling copper.
The triplexed works good if you have equipment. And I don't mean just a tugger, I'm talking having rollers and auto feeders. If you use manual labor the size of the reel (depending on the length, might offset the pros.
One more pro would be easier pull, obviously the triplexed will have lesser overall diameter and less likely to cross over than 4 individual conductors.
you want to pull triplexed 15 kv cable? why, on earth? how many pulls you making, and like was said, you ever seen what the spool something like this comes on?
what a PITA, in my not so humble opinion.
So when would it be beneficial to use triplexes cable? Overhead runs?