This is not a code question, and it (like the earlier question) does not make sense. What do you mean by "from B to ground"? What is "B"? To that I will add that a 120/240 volt, single phase system will not have 208 volts involved anywhere.What is the voltage from B to ground in the following system's
If you have three resistors connected in series (R1,R2,andR3) across a 180 volt supply,and the total voltage drop across R1 and R2 is 140 volt's,and the total across R2 and R3 is 100 volt's, and a Voltmeter
across R3 reads 40 volt's,how many volt's would you have across R1:_______; and alsoR2:______?
I have not started to work on the Answ. yet.
See how many guy's get this one right. For me, I have a hard time with these. 220.55 Is
easy to me.
We are not going to be able to help you, if you are not clearer in the description of the question. Your post #6 addresses a three phase, 4-wire, grounded-WYE system. In that type of system, the phase-to-phase voltage will be higher than the phase-to-ground voltage by a factor of the square root of 3 (approximately 1.732).Regarding the answer's For the B to ground Ques. are:
Then please don't ask us to help you with it. We are not here to do your work for you.I have not started to work on the Answ. yet.
The math is shown in post #11.With that, I don't get the math they used to come up the Answ.
Did I mention that this is NOT A CODE QUESTION?That is why they ask that type of Ques. To see how Code smart you are.
Yes you did.
Roger
A panelboard where we get 440 volt's from phase to phase. 3 PH., 4-wirs Sys., What's is the volt's
to ground from 1 phase. Answ. Key 440/1.73=254.34.
Mike didn't have anything in work book on this Cal.. Get Inf. on how this work's? We all know
about 1.732.
Thank's for the help on the square foot Ques. If we reverse the equation, I see how that work's
On the B to ground Ques., I went back on the Mike's DVD's and found it. First I guessed and
took 120/240 Ex., which I knew was 208. Did my math 208/240=.86666. Or 87 percent. I used
that as a multplyer on the Sec. voltage. Did the rest of the Ex. and it worked out just fine. Then
I found it on of Mike's DVD's where Dennis and Mike talked for a short time about around 87 percent
of the voltage of B phase to ground would show up on the meter.
On this Ques. with the resistors, I know that I am thinking to hard. I know that the total Res. of each
Res. equil's the total of applyed voltage. I have looked at Mike's Ex. and there isn't to much that help's
on this type of Ques.. I know that the Inf. on the VD. between the Res. is confusing me. A little help
(not the answer) to get me thinking not so hard. Thank's