Maybe you would like to show us the correct way to draw the diagram??
The correct answer cannot be determined until after the subtraction operation has occurred.
Technically all phasors should always have a positive magnitude with their angles being 'inverted' as needed, after all a line cannot truly have a negative length.
Mathematically it makes no difference, so this convention is usually reserved until the final step.
This is why I have said we do not really 'generate' a negative AC voltage, so if we calculate one, we have simply assigned it the wrong direction.
Van=Vnb=-Vna=-Vbn for a single center-tapped winding.
This is true only for vectors. For any other analysis method, (including phasor math) a negative magnitude is perfectly acceptable. And as you pointed out last night, you don't use graphical representations.Actually, the magnitude is ALWAYS positive.
I did. Jim overlooked something. Tail-to-tail occurs when one is a resultant phasor. That would be the 240 phasor which cannot exist for rattus.
The diagram is not correct for a basic phasor diagram. Rattus has drawn an origin shifted diagram. The flaw is evident because there's no origin tailed resultant.
A 240 resultant starting at the origin should appear somewhere. Either 120 phasor should be placed at the origin. Then the other phasor can be indicated by subtracting the 120 phasor from the resultant 240 phasor.
No 240 phasor from the origin means a misdrawn diagram.
Lets stay on topic.And, just how would you correctly draw the phasors for a 120V wye?
The reason why the discussion has gone on this long is because there are several posters here that can't distinguish "opinion" from "fact", and they present their "opinion" as though it is "fact". This raises the hackles of those people that don't subscribe to the same opinion. If the arguments were properly stated as being opinion-based, then this whole argument would vanish in minutes.For the life of me I cannot figure out why this is worth 240+ pages of bickering. Yes, the waveforms are 180 degrees out of phase, but it's an inversion, not a phase shift. It only looks like a phase shift because of the symmetry of the wave.
Lets stay on topic.
Three wye connected transfromers, is not the same as a single center-tapped winding where we have already agreed (?) Van=Vnb=-Vna=-Vbn.
Yes, my dear brainchild. That is graphics, and you stated last night that you do not employ graphics in your solutions. So which is it? Are you basing your responses on a graphical representation, or not?After all, a line cannot have a negative length!
Doesn't matter which node is which. At any instantaneous moment their polarities match. So:Which node is which? And, how come I get the right result by doing it wrong?
Again, whether you measure from the neutral or an endpoint, you have to draw your phasors based on instantaneous voltage. Rattus keeps discarding <180 by measuring each voltage source 1/2 cycle off.I'm afraid I don't understand your point. The two phasors are not "resultant" of anything. They are a model for the two windings of the transformer. They both use the neutral point as a common starting point. So, If Vna=120<180 and Vnb=120<0, Rattus' phasor diagram is correct. The resultant phasor from combining the two phasors would have a magnitude of 240. The angle of the resultant phasor would be dependent on which phasor was subtracted (tail-to-tail) from which.
Vab is the resultant phasor. Vnb and Vna are the component phasors. As voltages in series they are ADDITIVE not subtractive. You've discarded a 1/2 cycle to get Vna as 120<180 by neglecting the instantaneous voltage direction.Vab=Vnb-Vna = 120<0 - 120<180 = 240<0
Vba=Vna-Vnb = 120<180 - 120<0 = 240<180
Not correct. As drawn the expression should be Vab = Vnb + Vna = 0<0; In series the graphic lines are placed stacked. You shifted 1/2 cycle by lifting your pencil and moving back to the origin before drawing the second phasor.So as you see, the resultant phasor is 240V for Rattus' phasor diagram. It also properly models the transformer. The resultant phasor for a connection between A and B would be 240V<0 and the resultant phasor for a connection between B and A would be 240V<180. This is correct.
As stated above the origin has been shifted 1/2 cycle. The origin for a phasor diagram for a voltage series has no neutral point. It's not on the phasor diagram. Just an origin with phasors having magnitude and angle. The origin is NOT 0V and it's NOT the neutral. It's the beginning point of the diagram. The resultant is measured from the origin of the first phasor to the end point of the second phasor. Without the 1/2 cycle shift rattus's diagram would yield 0<?, with the shift it yields a resultant of 120<180 measured on the graph.The origin hasn't "shifted" anywhere. The origin for both phasor is the neutral point. There is no need for there to be a origin tailed resultant. The resultant 240V phasor is measured from head to head of the two base phasor. This is fine under basic vector math. There is no need to force the diagram into a head-to-tail arrangement.
That would be the correct phasor diagram for Van=120<0 and Vnb=120<0. It would be incorrect for Vna=120<180 and nb=120<0.
The correct diagram for Vna=120<180 and Vnb=120<0 would be: <-----------.----------->
Both of these phasor diagrams are correct for their base phasors, and both provide the same (and correct) resultant phasor when combined.
Then let's talk about facts. With a transformer, one does not have to have a time shift to have a phase shift.The reason why the discussion has gone on this long is because there are several posters here that can't distinguish "opinion" from "fact", and they present their "opinion" as though it is "fact".
Not really the first time. Just the first time it has been pretty much contained within one thread instead of spawning more threads.2400+ replies.
Really?
I think we all agree you were right at the beginning.Is anyone any closer to agreement?
Forgive me. I did not read your whole response, but your diagram is useful. This is not necessarily directed at you.Doesn't matter which node is which. At any instantaneous moment their polarities match. So:
A -----------> N
N -----------> B
A -----------+-----------> B
or
A <----------- N
N <----------- B
A <-----------+----------- B
Voltages in series are additive not subtractive.
A -----------> N
N -----------> B
or
A <----------- N
N <----------- B
A -----------> N
N -----------> B
What some respondents in this thread may not realize is that Rattus brought this particular aspect up many times in the past as it relates to summing KVL around a loop. When it was brought to his attention that his vectors did not conform to KVL, his response was that when he encountered tail-to-tail vectors that it meant subtraction. As was demonstrated last night, tail-to-tail is an inappropriate method for signifying subtraction because it is indeterminate.
He presents his position from a graphical perspective, but then denies ever using graphical methods. This is why so many of us keep pointing out his hidden minus sign that he doesn't want anyone else to notice.