I wasn't trying to be "smart" just inquisitive,
I agree that it is a Art 230 not Art 240 based on the "tap" definition. Likewise I have seen (and possibly approved) similar
situations where the conductors were installed in Rigid and did not leave the electric room.
	
		
			
		
		
	
				
			I agree that it is a Art 230 not Art 240 based on the "tap" definition. Likewise I have seen (and possibly approved) similar
situations where the conductors were installed in Rigid and did not leave the electric room.
 
				
 
 
		 
 
		