Disconnect for seperate structure and MWBC

Status
Not open for further replies.

ner

Member
Location
connecticut
Our town is still using the 2005 NEC. What code year and article requires a disconnect switch for a MWBC to a shed or barn? Where is the disconnect switch located? Is a two pole breaker used at the source or does a disconnect switch need to be installed in the shed or barn? The plan calls for a 20 amp two circuit MWBC from a 120/208 source. What code year and article requires a MWBC to a shed or barn? Why cant two circuits (two hots and two neutrals) be used instead of a MWBC?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Lot at once :D

225.30 - 39 have the answer to most of your questions.
Note a MWBC is considered 1 circuit by this section./
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The switch at the barn can be a double pole switch if this is residential property. I don't know why the code only allows one circuit but it does so we must follow it. I usually come up on the exterior and install a weatherproof setup with a dp switch and then feed the circuits from there.
 