Disconnect for seperate structure and MWBC

Merry Christmas
Status
Not open for further replies.

ner

Member
Location
connecticut
Our town is still using the 2005 NEC. What code year and article requires a disconnect switch for a MWBC to a shed or barn? Where is the disconnect switch located? Is a two pole breaker used at the source or does a disconnect switch need to be installed in the shed or barn? The plan calls for a 20 amp two circuit MWBC from a 120/208 source. What code year and article requires a MWBC to a shed or barn? Why cant two circuits (two hots and two neutrals) be used instead of a MWBC?
 
Lot at once :D

225.30 - 39 have the answer to most of your questions.
Note a MWBC is considered 1 circuit by this section./
 
The switch at the barn can be a double pole switch if this is residential property. I don't know why the code only allows one circuit but it does so we must follow it. I usually come up on the exterior and install a weatherproof setup with a dp switch and then feed the circuits from there.
 